In this case, I've connected the UPS to a Raspberry Pi running Raspbian 8 (Jessie).
1) Connect the UPS to power
Seems obvious, but still...
2) Connect USB
Then, connect the USB cable and make sure it shows up on the computer side:
3) Install apcupsd:ID 051d:0002 American Power Conversion Uninterruptible Power Supply
On Debian-based systems (including e.g. Ubuntu), it's as easy as this:
Code: Select all
$ apt-get install apcupsd
Make a backup of "/etc/apcupsd/apcupsd.conf" and then open it in a text editor.
For USB connection, edit the settings to this:
(Change "UPSNAME" to whatever you like )
Code: Select all
UPSNAME MyUPS
UPSCABLE usb
UPSTYPE usb
DEVICE
POLLTIME 60
5) Enable autostart of apcupsd during boot:
In "etc/default/apcupsd", change "ISCONFIGURED" to yes:
Save the file.ISCONFIGURED=yes
This tells the system that apcupsd is to be started as a service.
Without it you also won't be able to start it using the command "service apcusd ...".
6) Restart the apcupsd:
In order to apply the changed configuration, you need to start (or restart) the apcupsd service:
Code: Select all
$ sudo service apcupsd restart
Code: Select all
$ sudo apcaccess status
Code: Select all
APC : 001,036,0874
DATE : 2016-12-15 19:44:19 +0100
HOSTNAME : rasputin2
VERSION : 3.14.12 (29 March 2014) debian
UPSNAME : rasputin2
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2016-12-15 19:18:12 +0100
MODEL : Back-UPS XS 950U
STATUS : ONLINE
LINEV : 226.0 Volts
LOADPCT : 0.0 Percent
BCHARGE : 100.0 Percent
TIMELEFT : 320.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : Medium
LOTRANS : 155.0 Volts
HITRANS : 280.0 Volts
ALARMDEL : 30 Seconds
BATTV : 13.5 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x05000008
SERIALNO : 3B1629X20043
BATTDATE : 2016-07-22
NOMINV : 230 Volts
NOMBATTV : 12.0 Volts
NOMPOWER : 480 Watts
FIRMWARE : 925.T2 .I USB FW:T2
END APC : 2016-12-15 19:44:47 +0100